Building inspector won't let me spray
I need a product that has the ERS testing, opencell, and an r-value of 4 0r more. preferably like a 1lb or 1.2lb. Thank you
mason
Posted: Aug 23, 2010 12:00 PM
Go to this website and check out the various supplier's ES reports.
http://www.icc-es.org/reports/index.cfm?list=list

I found one that is listed at 4.1 at one inch but at 3 inches totals R 11. Open cell foam tends to have less R value per inch at thicker applcations

OK, I found a total of 4 systems that report 4.0 or higher R values at one inch and 2 that have 4.0 R value per inch at 4 inches or more.

These are the reports.
NCFI ESR 1154. R value 4.1 at one inch but 3.7 per inch at 3.5 inches
Demilec ESR 2600 R value 4.6 at one inch and 17.8 at 4 inches (4.45 per inch)
Gaco Western ESR 2478 4.2 at one inch and at 3.9 per inch at 4 inches
Urethane Soy Systems 4.0 at one inch at 4.27 per inch at 4 inches.

Let me know if I missed a few.