Q&A Forums
Thermal Barrier Update? Post New Topic | Post Reply
Author | Comments |
---|---|
Caleb DeFord
Posted: Aug 08, 2012 11:09 AM
|
Thermal Barrier Update?
Hey Mason,I just got an email stating that .016 inch steel qualifies as a thermal barrier...and "3/8 gypsum"....and 1/4 inch hardboard???? I thought it had to be 1/2 inch drywall or 3/4 inch plywood. I would appreciate your feedback very much. Thanks, Dr. Know.;-) See Page 8 of SPFA "Thermal Barriers" document for reference if needed. -Foamilyman |
mason
Posted: Aug 10, 2012 10:26 AM
|
No,the code hasn't changed. Those materials are listed in the building codes as acceptable ignition barriers in crawl spaces and attics, not thermal barriers for the inhabited areas of the building. |